Problemy z serią MOXA NPort 5000 - Jak wysyłać polecenia?

Switche przemysłowe, media konwertery ethernetowe

Moderatorzy: Marek Sikora, Lukasz Szymczak

Re: Problemy z serią MOXA NPort 5000 - Jak wysyłać polecenia?

Postprzez Moxa-PiotrG » Cz, 28 sty 2021, 08:13

Hi Bucher,

The Most popular operation mode is RealCOM. In this mode user is mapping virtual COM port by Nport Windows Driver Manager software on computer
Fallowing conditions must be met to make connection:
-Nport set to RealCOM mode
-IP address of Nport and PC must be in the same network subnet
-Firewall in OS must allow outgoing connection with destination TCP ports: 950+x(max.16), 966+x(max. 16).
-Virtual COM port mappedon OS by Nport Windows Driver Manager or Nport Administrator

You can also find description in below producer technote:
https://www.moxa.com/getmedia/90269b7f-b656-41b7-8b9c-94e030761b28/moxa-real-com-mode-for-nport-tech-note-v1.1.pdf
Pozdrawiam,
Piotr Gocłowski
Elmark Automatyka
Moxa-PiotrG
 
Posty: 56
Dołączył(a): Pn, 28 maja 2012, 11:13

Powrót do Przemysłowy Ethernet



Kto przegląda forum

Użytkownicy przeglądający to forum: Brak zalogowanych użytkowników i 1 gość